kohler generator shuting off-whats up?
#1
Banned
Thread Starter
Join Date: Dec 2003
Location: st. louis,mo.
Posts: 1,647
Likes: 0
Received 0 Likes
on
0 Posts
kohler generator shuting off-whats up?
have a nearly new kohler generator that starts fine ,runs for about 5 minutes and just shuts off. changed spark plugs, oil is fine just a little over full. is there a auto shutoff on them for some condition?
#4
Registered
Join Date: Sep 2001
Location: Houston, TX, USA
Posts: 2,287
Likes: 0
Received 0 Likes
on
0 Posts
I agree with the two responces above. After 5 minutes it gets too warm without proper cooling. Most likely cause is bad impeller in water pump or hull intake is plugged.
#5
Registered
There's an auto shut off on all generatrs. Kohler generators shut down due to high coolant temp, low oil pressure, overspeed, maybe high exhaust temp. Check the gauges when it shuts down.
Gary
Gary
#6
Charter Member #1171
Charter Member
I agree,,,,,,, start it up and look for water coming out of its exhaust to confirm or elimintae the impeller.
Easiest way to diag
Easiest way to diag
__________________
I want to live in a world where a chicken can cross the road and not have its motives questioned.
I want to live in a world where a chicken can cross the road and not have its motives questioned.
#7
Registered
Join Date: Jun 2007
Posts: 68
Likes: 0
Received 0 Likes
on
0 Posts
I had the same problem with my 7.3 Kohler. I found my oil filter wasn't tight and leaked which caused the oil level to drop below a certain level .Kohler has an automatic safety shut off for low oil level. I'll bet that's your problem.......